All AC problems
Troubleshooting · Heat pumps in winter

Heat Pump Not Heating or Blowing Cold Air? What to Check First

It runs in winter, but the house stays cold or the vents blow cool air.

By ·Updated

Most likely causes

  1. Thermostat on Cool or Auto, or a schedule holding a low temperature
  2. A defrost cycle in progress (cool air for a few minutes is normal)
  3. A clogged air filter
  4. The outdoor unit iced over or blocked by snow
  5. Backup (auxiliary) heat not working on the coldest days
  6. A reversing valve stuck in cooling mode, or low refrigerant

Before you open anything

Turn the system off at the thermostat, then switch off power at the breaker and at the disconnect beside the outdoor unit. Never touch the capacitor, even with the power off: it can hold a dangerous charge. Refrigerant work is for licensed technicians only. Reset a tripped breaker once; if it trips again, leave it off.

Heat strips run on a separate high-voltage circuit; don't open the air handler to check them. Never add refrigerant yourself: it requires EPA certification, and newer systems use mildly flammable refrigerants.

Check these first (free, 5 minutes)

  • Thermostat: mode on Heat, set at least 2–3°F above the room, schedule or "hold" off. A heat pump thermostat may show "Aux" or "Em Heat"; leave Emergency Heat off for now.
  • Feel the air at a vent after 10 minutes of running. Heat pump air feels lukewarm compared with a gas furnace; that's normal as long as the house slowly warms.
  • Outdoor unit: is the fan spinning and is it free of thick ice and snow? A short burst of steam with the fan stopped is a normal defrost.
  • Air filter: replace it if it's gray. Low airflow cuts heating just as it cuts cooling.
  • Breakers: there are usually separate breakers for the outdoor unit, the indoor air handler and the backup heat strips.

Causes, signs and repair costs

Thermostat settings or schedule

DIY

Mode on Cool or Auto with a low setpoint, a schedule or vacation hold

Typical cost: $0

Normal defrost cycle

DIY

Cool air for a few minutes, outdoor fan stopped, steam rising from the unit, then heat resumes

Typical cost: $0 (normal)

See: Heat pump steaming / defrost →

Clogged filter

DIY

Weak airflow from vents, filter visibly gray

Typical cost: $5–$20

Outdoor coil iced over or buried in snow

DIY or pro

Coil encased in ice that doesn't clear, or snow drifted against the unit

Typical cost: $0 to clear snow; depends on the cause

See: Heat pump iced up →

Outdoor unit not running

DIY or pro

Indoor fan runs, outdoor unit silent or humming; breaker off

Typical cost: $0 (breaker) to $150–$400 (capacitor)

See: Outdoor unit not running →

Backup heat not working

Pro

House falls behind only on the coldest days; "Aux" shows but the air stays lukewarm; heat-strip breaker tripped

Typical cost: $75–$200 service call plus parts

Reversing valve stuck in cooling

Pro

Air from the vents is cold, not just lukewarm, all the time in Heat mode; the outdoor unit blows warm air

Typical cost: $350–$1,200

Low refrigerant (a leak)

Pro

Heating has gotten weaker over weeks, frequent icing, hissing or oily spots on the lines

Typical cost: $400–$2,400 to find, fix and recharge

Typical U.S. installed prices in 2026. Most repairs also carry a service call fee of $75–$200, often credited toward the repair. See AC repair costs in 2026 for the full list.

Step by step

  1. 1

    Set the thermostat correctly

    Set it to Heat, 2–3°F above the room temperature, fan on Auto, and turn off any schedule or hold. If it was on Cool or Auto with a low setting, that alone explains cold air.

  2. 2

    Rule out a defrost cycle

    In cold, damp weather a heat pump reverses for a few minutes to melt frost off the outdoor coil. During defrost the outdoor fan usually stops, the unit may steam, and the indoor air can feel cool. If heat returns within about 15 minutes, nothing is wrong.

  3. 3

    Replace the filter and open the vents

    A clogged filter or closed vents cut airflow, which makes a heat pump run hotter and less efficiently and can trip its safety controls. Fit a new filter and make sure supply and return grilles are open and clear.

  4. 4

    Clear the outdoor unit

    Brush snow off the top and sides and keep 2 feet clear around it. If the coil is solidly encased in ice that a defrost doesn't clear, see the frozen outdoor unit page. Don't chip ice off the coil.

  5. 5

    Use Emergency Heat only if the outdoor unit has failed

    Emergency Heat turns the heat pump off and heats with the backup heat alone, usually electric strips that cost about two to three times as much to run. It's the right setting to stay warm while you wait for a technician, not an everyday setting.

Call a technician if

  • The air is cold, not lukewarm, for more than 15 minutes in Heat mode
  • The outdoor unit stays encased in ice after a defrost cycle
  • The house can't keep up even on mild winter days
  • A breaker for the outdoor unit or the heat strips trips again after one reset

Red flags on a quote

  • A refrigerant top-up with no leak search: heat pumps don't use up refrigerant
  • A reversing valve replacement quoted before anyone has checked the thermostat wiring and the valve's solenoid coil, which are cheaper fixes
  • A new system quoted because "heat pumps don't work in the cold": cold-climate models are rated to heat well below freezing

Facing an expensive repair on an older system? Run it through the repair vs replace calculator, or read the $5,000 rule.

Is a heat pump worth it where you live?

Whether a heat pump saves money over a furnace depends on what you heat with now and what you pay for electricity. Our heat pump vs central AC guide runs the numbers for gas, propane, oil and electric baseboard heat.

See Heat pump vs central AC: what it costs to run.

Frequently asked questions

Why is my heat pump blowing cold air?

Most often it's in a defrost cycle, which lasts a few minutes and then heat returns. If the air stays cold, check that the thermostat is on Heat and set above the room temperature. Air that is cold all the time in Heat mode can mean the reversing valve is stuck in cooling, which needs a technician.

Is it normal for heat pump air to feel lukewarm?

Yes. A heat pump delivers a larger volume of moderately warm air rather than short blasts of hot air like a gas furnace, so the air at the vent can feel only lukewarm against your hand. As long as the house reaches the set temperature, it's working.

Should I switch my heat pump to Emergency Heat when it's very cold?

Usually not. The thermostat brings in backup (auxiliary) heat automatically when the heat pump needs help. Emergency Heat turns the heat pump off entirely, which costs much more to run. Use it only when the outdoor unit has failed or is iced solid and you're waiting for a repair.

At what temperature does a heat pump stop heating?

It depends on the model. Older and standard heat pumps lose a lot of capacity below about freezing and lean on backup heat, while cold-climate models are designed to keep heating at 5°F (−15°C) and below. Check the low-temperature rating on your model's spec sheet.

Related problems

Fixed it? Check what it costs to run

If your system is old enough to keep breaking, compare its running cost with a new one before the next repair.

Open the SEER savings calculator

Stop Overpaying for Heating & Cooling.

The most expensive HVAC repair is the one that catches you off guard in July. Get our free HVAC Maintenance & Savings Checklist — seasonal checklists for central AC, furnaces, and ductless mini-splits, a complete filter selection guide, and the 5 questions to ask your technician before agreeing to any repair or replacement.

Free download. No spam, ever.